I have to replace 6 pitch boxes on a touring van caravan  site.

So six pitch boxes with 4 van hookup points per box, each hookup point protected by a 10A 30mA RCCB.

Unfortunately I've also discovered that the site is wired as a ring in 6mm SWA, buried direct in ground.


Any thoughts on max fuse size to protect a 6mm ring?


Regards

George
Parents
  • You could arrive on a camp site and charge your EV from the pitch socket protected by the 10 amp MCB, just so long as you are not planning to drive it for twenty four hours or so and you are not trying to use a multiway adapter to try and supply something else at the same time.


    It's going to happen.


    Andy B.
Reply
  • You could arrive on a camp site and charge your EV from the pitch socket protected by the 10 amp MCB, just so long as you are not planning to drive it for twenty four hours or so and you are not trying to use a multiway adapter to try and supply something else at the same time.


    It's going to happen.