This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Cables in heating voids

Hi Folks,


'intresting' day today...


So at the moment I am replacing a 150kW gas warm air unit, a huge thing in a commercial building.


Today I finished ripping out the old unit (146kW) the system draws in fresh air from outside and distributes the warm air via a network of underground ducts, really they are just concrete tunnels large enough to crawl through.


So being inquisitive and not being able to resist this unknown hole to somewhere in the floor of the plant room I stuck my ladders down there and went for a wander (pig in sh*it comes to mind ?) as soon as I get in there are 4 25mm galve conduits (building lighting 10x 10A) and a 25 2c SWA (feeding a kitchen sub 100A) with a 10mm earth attached snaking through there, I wander further 25m ish still the armoured and conduits but also a few fire alarm cables have entered the scene.


Swa -90's

Conduits - either 73 or 90's


Clearly a very convienient route for cables and none of them are showing any outward signs of distress (cant see in the galv conduits ofcourse)


Thoughts? Just canvasing opinion...
Parents
  • As Andy says, the ducts are distributing warm air rather than hot. The cables should be rated for an ambient of at least 30 degrees. The life may be reduced by having a higher average ambient through the year but it would still be years before I would expect to see a difference and if this is taken into account at the design stage it is certainly not a problem. The fact that they are better positioned for inspection or replacement may counter any disadvantage. The added advantage is that a bit of heat dissipation from the cables will marginally (but probably not noticeably) reduce your heating bill.

    Alasdair
Reply
  • As Andy says, the ducts are distributing warm air rather than hot. The cables should be rated for an ambient of at least 30 degrees. The life may be reduced by having a higher average ambient through the year but it would still be years before I would expect to see a difference and if this is taken into account at the design stage it is certainly not a problem. The fact that they are better positioned for inspection or replacement may counter any disadvantage. The added advantage is that a bit of heat dissipation from the cables will marginally (but probably not noticeably) reduce your heating bill.

    Alasdair
Children
No Data