Hello All

We all know the benefits of RCD protection and how the regulations are changing regarding domestics. I am constantly being asked if RCDs are required for normal switched socket circuits in industrial installations apart from the obvious use of RCDs for areas likely to cause a reduction in resistance (sockets that could conceivably be used out side). So are RCDs required for general office circuits, for dedicated IT equipment (computers etc), work areas such as clean dry packing areas and so on.


Given RCDs require testing regularly and the results recorded which causes disruption to production equipment, IT equipment, Data centers etc are RCDs really required especially if they are installed within steel conduit or steel trunking on walls or under floors?


Any advice welcome


Andy
Parents
  • Former Community Member
    0 Former Community Member
    The issue I have is the use of RCDs in a high volume production environment, switching of this equipment for testing is problematic not just in down time but re calibration of equipment and that's not to mention nuisance tripping.


    One assumes you have full a UPS system in place?


    Regards


    BOD
Reply
  • Former Community Member
    0 Former Community Member
    The issue I have is the use of RCDs in a high volume production environment, switching of this equipment for testing is problematic not just in down time but re calibration of equipment and that's not to mention nuisance tripping.


    One assumes you have full a UPS system in place?


    Regards


    BOD