davezawadi:
Andy
Consider carefully the OP and the real circuit. It has a 40A CPD and if installed correctly a 10mm2 cable. But lets assume it has a 6mm cable buried in a wall or somewhere clipped direct. The shower is obviously satisfactory and probably takes 37A. The oven could potentially take another 16A or so and you are screaming (or actually Alcomax) that the cable could melt. Could it? A 40 A breaker actually trips quickly at at least 52A so our customer should never get a trip.
Regards
David
davezawadi:
Andy
Consider carefully the OP and the real circuit. It has a 40A CPD and if installed correctly a 10mm2 cable. But lets assume it has a 6mm cable buried in a wall or somewhere clipped direct. The shower is obviously satisfactory and probably takes 37A. The oven could potentially take another 16A or so and you are screaming (or actually Alcomax) that the cable could melt. Could it? A 40 A breaker actually trips quickly at at least 52A so our customer should never get a trip.