Two high-power appliances on a single 40A RCD

Former Community Member
Former Community Member
I have an electric shower installed on a 40A RCD, in a room adjacent to my kitchen. The shower is only used in an emergency - i.e. when our gas boiler is unable to provide hot water to our main bathroom. I would like to take a spur from this 40A connection to use for a new double oven, which is rated at 32A. Can anyone advise on a safe and legal way to do this, ensuring that only one of the two appliances can be connected at any one time?
Parents

  •  It has a 40A CPD and if installed correctly a 10mm2 cable. But lets assume it has a 6mm cable buried in a wall or somewhere clipped direct. The shower is obviously satisfactory and probably takes 37A. The oven could potentially take another 16A or so and you are screaming (or actually Alcomax) that the cable could melt. Could it? A 40 A breaker actually trips quickly at at least 52A so our customer should never get a trip.



    Why would "installed correctly" require 10sq.mm.?

    Assuming, as you say, method C and 37A, then 4sq.mm. would be adequate.


    On the other hand if it does have 10sq.mm. cable and method C, then change the CPD to 63A and all is compliant.
Reply

  •  It has a 40A CPD and if installed correctly a 10mm2 cable. But lets assume it has a 6mm cable buried in a wall or somewhere clipped direct. The shower is obviously satisfactory and probably takes 37A. The oven could potentially take another 16A or so and you are screaming (or actually Alcomax) that the cable could melt. Could it? A 40 A breaker actually trips quickly at at least 52A so our customer should never get a trip.



    Why would "installed correctly" require 10sq.mm.?

    Assuming, as you say, method C and 37A, then 4sq.mm. would be adequate.


    On the other hand if it does have 10sq.mm. cable and method C, then change the CPD to 63A and all is compliant.