has anybody mentioned the D word?
Put another way, you have two 40 A showers, and a 40 A cooker on a 100 A supply. Does that break the rules?
By example take the cables in your street. They are probably protected by a 600A fuse and feed many houses. You may have a 10mm2 service if you have an old house (I used to some years back). A short on the service cable can be quite spectacular because the short circuit rating is quite suspect at a 5kA fault. If each house takes power and it exceeds about 1kA for a reasonable period the 600A fuse will blow, but it takes time. The street cable will not really be warm. If they all have off peak heating and 800A flows all night (not unusal) the cable will be pretty hot by morning. Is our little used shower a problem, very unlikely.
Can anyone advise on a safe and legal way to do this, ensuring that only one of the two appliances can be connected at any one time?
What is wrong with simultaneous use, it will trip the MCB at some point, strangely that is what the MCB is for!!!!
The screwfix forum says
433.1.1 [i] the rated current of the protective device is not less than the design current.
It is one thing to say something is not going to be used. It is still there and could be used. The kitchen fitter is being responsible; why should they take on additional risk?
The answer by Broadgage concerning "Shower priority unit" is a legitimate way to go. For legitimate, read sensible.
Circuit breaker as a "load limiter" is a bit rough; for the cavalier it may be a badge of honour , but really should have no place for installation work done for reward and done to some kind of standard.
Say I have a large motor circuit say 100 kW which is designed to start a few times per hour. I use a type D (MCCB but this is to help you) CPD. Do the cables need to be rated at 6 times the running current? If so which regulation are you quoting? Just some background this motor may take a minute (60 seconds) to reach FLC due to the load inertia. What size cables should I use? How do I control the number of starts per hour? How is this different to the example I gave or the OP?
has anybody mentioned the D word?
Put another way, you have two 40 A showers, and a 40 A cooker on a 100 A supply. Does that break the rules?
By example take the cables in your street. They are probably protected by a 600A fuse and feed many houses. You may have a 10mm2 service if you have an old house (I used to some years back). A short on the service cable can be quite spectacular because the short circuit rating is quite suspect at a 5kA fault. If each house takes power and it exceeds about 1kA for a reasonable period the 600A fuse will blow, but it takes time. The street cable will not really be warm. If they all have off peak heating and 800A flows all night (not unusal) the cable will be pretty hot by morning. Is our little used shower a problem, very unlikely.
Can anyone advise on a safe and legal way to do this, ensuring that only one of the two appliances can be connected at any one time?
What is wrong with simultaneous use, it will trip the MCB at some point, strangely that is what the MCB is for!!!!
The screwfix forum says
433.1.1 [i] the rated current of the protective device is not less than the design current.
It is one thing to say something is not going to be used. It is still there and could be used. The kitchen fitter is being responsible; why should they take on additional risk?
The answer by Broadgage concerning "Shower priority unit" is a legitimate way to go. For legitimate, read sensible.
Circuit breaker as a "load limiter" is a bit rough; for the cavalier it may be a badge of honour , but really should have no place for installation work done for reward and done to some kind of standard.
Say I have a large motor circuit say 100 kW which is designed to start a few times per hour. I use a type D (MCCB but this is to help you) CPD. Do the cables need to be rated at 6 times the running current? If so which regulation are you quoting? Just some background this motor may take a minute (60 seconds) to reach FLC due to the load inertia. What size cables should I use? How do I control the number of starts per hour? How is this different to the example I gave or the OP?