This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Two high-power appliances on a single 40A RCD

Former Community Member
Former Community Member
I have an electric shower installed on a 40A RCD, in a room adjacent to my kitchen. The shower is only used in an emergency - i.e. when our gas boiler is unable to provide hot water to our main bathroom. I would like to take a spur from this 40A connection to use for a new double oven, which is rated at 32A. Can anyone advise on a safe and legal way to do this, ensuring that only one of the two appliances can be connected at any one time?
Parents
  • Is the existing oven gas or electric?


    Is the existing oven supplied by a plug from socket circuit or goes it have its own circuit, if it foes have its own circuit what size is the cable and the protective device got it in the consumer unit?


    Exactly what oven have you bought?


     Andy Betteridge 


Reply
  • Is the existing oven gas or electric?


    Is the existing oven supplied by a plug from socket circuit or goes it have its own circuit, if it foes have its own circuit what size is the cable and the protective device got it in the consumer unit?


    Exactly what oven have you bought?


     Andy Betteridge 


Children
No Data