Two high-power appliances on a single 40A RCD

Former Community Member
Former Community Member
I have an electric shower installed on a 40A RCD, in a room adjacent to my kitchen. The shower is only used in an emergency - i.e. when our gas boiler is unable to provide hot water to our main bathroom. I would like to take a spur from this 40A connection to use for a new double oven, which is rated at 32A. Can anyone advise on a safe and legal way to do this, ensuring that only one of the two appliances can be connected at any one time?
Parents
  • The calculation based on the requirements of BS7671


    Rating on plate 4.0 kW


    So 17.4 amps at 230 volts.


    Therefore 10 amps plus 30% of 7.4 amps gives an assumed current demand of 12.3 amps


    So is everyone satisfied with having a double pole B16 MCB in a metal enclosure connecting the oven to a 32 amp socket ring circuit, rather than increasing the potential load on the shower circuit by over 12 amps?


     Andy Betteridge 


Reply
  • The calculation based on the requirements of BS7671


    Rating on plate 4.0 kW


    So 17.4 amps at 230 volts.


    Therefore 10 amps plus 30% of 7.4 amps gives an assumed current demand of 12.3 amps


    So is everyone satisfied with having a double pole B16 MCB in a metal enclosure connecting the oven to a 32 amp socket ring circuit, rather than increasing the potential load on the shower circuit by over 12 amps?