Good morning everyone.
This is a theoritical question that I have however come across....really a lot when inserting my loads in Amtech!!!!!
I have a DB which feeds lighting and small power in a reception area in a hotel.
The DB has various lighting circuits and various small power circuits (sockets, door access controllers, heaters, automatic doors etc etc etc)
As I understand there is one type of diversity that is common sense and is the "concurrency factor" which is applied to the DB as a whole.
I am more interested however in additional diversities for the individual circuits.
My question is this.
I have a room where the lights are all on or all off through presence detection. I anticipate that within a typical day the lights will be on 6 hours. That is 25% of the day. Does this mean that I sould insert for this specific circuit an individual diversity factor of 0.25?
Do I interpret this correctly?