broadgage:
There is a general acceptance that 13 amp plugs and sockets can not reliably and continually carry more than about 10 amps. Therefore domestic appliances are in practice limited to about 10 amps, presumably to avoid warranty claims about melted plugs.
The main exception is electric kettles, these are used so briefly that a full 13 amps is fine. Table top electric cookers are sometimes a full 13 amps, under worst case conditions, but much less most of the time and again are fine in practice.
Large steam clothes irons are not common domestically, but should also be fine as continual full load operation is unlikely. I have seen steam irons in a tailors workshop that require two 13 amp supplies. One for the iron itself, actual loading about 5 amps, and a second supply for the remote steam generator, actual loading about 12 amps. Often both plugged into the same socket with a death cube.
Domestic appliances likely to run continually are unlikely to exceed 10 amps these days.
3Kw heaters are still available but are marketed as being for industrial use and are therefore supplied without a plug. No warranty claims about melted plugs if plug not supplied.
broadgage:
There is a general acceptance that 13 amp plugs and sockets can not reliably and continually carry more than about 10 amps. Therefore domestic appliances are in practice limited to about 10 amps, presumably to avoid warranty claims about melted plugs.
The main exception is electric kettles, these are used so briefly that a full 13 amps is fine. Table top electric cookers are sometimes a full 13 amps, under worst case conditions, but much less most of the time and again are fine in practice.
Large steam clothes irons are not common domestically, but should also be fine as continual full load operation is unlikely. I have seen steam irons in a tailors workshop that require two 13 amp supplies. One for the iron itself, actual loading about 5 amps, and a second supply for the remote steam generator, actual loading about 12 amps. Often both plugged into the same socket with a death cube.
Domestic appliances likely to run continually are unlikely to exceed 10 amps these days.
3Kw heaters are still available but are marketed as being for industrial use and are therefore supplied without a plug. No warranty claims about melted plugs if plug not supplied.