davezawadi:
I used to have an MK safetyplug on my 180A stick welder, perhaps a 10 kW appliance with a solid fuse fitted. It never overheated despite some fairly heavy and extended use. Products today are just plain useless, but made to BS EN standards of course.
Chris Pearson:
This plug (with bottom, sides, and top) was on a 3 kW heater. I suspect that the over-heating may have been in part due to inadequate insertion leading to arcing. I cannot see why the pins would run so much hotter than the cable.
Simon Barker:
Chris Pearson:
This plug (with bottom, sides, and top) was on a 3 kW heater. I suspect that the over-heating may have been in part due to inadequate insertion leading to arcing. I cannot see why the pins would run so much hotter than the cable.
The problem with 13A plugs is that they have a built-in heating element, in the form of a BS1362 fuse. At currents that would cause any other design of plug to get a bit warm, the fuse in a BS1363 plug can produce a significant amount of heat, which is then trapped inside a well-insulated enclosure.
davezawadi:
Interesting that both pins got very hot (well probably over 70C). I wonder what the pins are made of, perhaps high resistance material. Brass is expensive now! I don't see much sign of arcing on the pins, they usually get discoloured and pitted if this happens. Did the socket survive the onslaught?