1
Do i need to have RCD protection on all of the 3 phase sockets
Also the board currently supplies a 3 phase compactor outside of the workshop via a socket- Am i right in saying if i replace the socket with an isolator and hardwire it this will negate the need for a RCD.
I am the engineering manager at a bakery and we are planning to re-wire our work shop........ .. I'm trying to design it in such a way that doesn't require me needing a board twice the size we have in place at the moment.
mapj1:
3 phase (4 pole ) RCBOs exist combining an RCD and MCB function,
Doepke certainly do them example , as I think do Hagar (in some configurations).
When I last looked the Schneider Siemens derived solution was a to suggest a 3 phase MCB, plus an external shunt trip driven by a VIGI
configured as a residual current sensor, which in comparison is a bit primitive.
Since then ABB have released these
mapj1:
You may RCD at the socket, if you wish to and if the wiring from the main board to that point does not need an RCD - SWA or singles in steel conduit would not for example. It could be the local isolation.