This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Maximum size of solar panels

I was just wondering if it's still the case that solar panel installations are rated to  16 amps  single phase does this apply to all single phase generators on domestic installations
Parents
  • There is no limit on the capacity of a stand alone PV array. I know of one that is 20 Kw.

    The 16 amps per phase is the standard limit for domestic and similar grid tied PV arrays. Much larger grid tied arrays are possible but the permission and approval process is much more complex.

    There are grid tied solar farms with outputs of hundreds of kw, and AFAIK nothing prohibits anyone from building one, subject to obtaining all required permits and approvals. A dedicated substation would probably be required, and maybe reinforcement of the distribution network.

     

    The rues in Ukraine may differ of course.

Reply
  • There is no limit on the capacity of a stand alone PV array. I know of one that is 20 Kw.

    The 16 amps per phase is the standard limit for domestic and similar grid tied PV arrays. Much larger grid tied arrays are possible but the permission and approval process is much more complex.

    There are grid tied solar farms with outputs of hundreds of kw, and AFAIK nothing prohibits anyone from building one, subject to obtaining all required permits and approvals. A dedicated substation would probably be required, and maybe reinforcement of the distribution network.

     

    The rues in Ukraine may differ of course.

Children
No Data