What earthing arrangement is this?

Former Community Member
Former Community Member
The supply is from a private transformer in a four core cable 3ph + n. The cable armour is earthed and connected to the MET. However there is also a green and yellow cable connected to the neutral terminal at the main isolator going back to a the transformer casing. The transformer is only 5 or 6 metres away. I think this must have been intended to make it a tncs supply but seems to me to just create parallel neutral conductors. Or is it tn-s-c-s?  I have only been able to go off visual inspection because I could not disconnect the supply..
Parents

  • Johno12345:

    . . . its not combined though, Ill have to check but I think its got a link between N and the transformer frame in the spreader box too . . . 




    If it does have a second link, then it is TNC-S. 


    Regards,


    Alan. 

Reply

  • Johno12345:

    . . . its not combined though, Ill have to check but I think its got a link between N and the transformer frame in the spreader box too . . . 




    If it does have a second link, then it is TNC-S. 


    Regards,


    Alan. 