What earthing arrangement is this?

Former Community Member
Former Community Member
The supply is from a private transformer in a four core cable 3ph + n. The cable armour is earthed and connected to the MET. However there is also a green and yellow cable connected to the neutral terminal at the main isolator going back to a the transformer casing. The transformer is only 5 or 6 metres away. I think this must have been intended to make it a tncs supply but seems to me to just create parallel neutral conductors. Or is it tn-s-c-s?  I have only been able to go off visual inspection because I could not disconnect the supply..
Parents
  • Chris


    Apart some special circumstances you are not allowed to combine the neutral and earth in the consumers installation.  The "S" in TN- C- S means separate. So we colour our protective conductors green/yellow even if they are connected to the supply neutral.


    I am a bit sceptical about the arrangement in the OP. Having a neutral coloured green/yellow run outside a SWA armour with one inside is a bit worrying! Running a separate earth with SWA or AWA cables is common practice but they are connected to the earth bar not the neutral.
Reply
  • Chris


    Apart some special circumstances you are not allowed to combine the neutral and earth in the consumers installation.  The "S" in TN- C- S means separate. So we colour our protective conductors green/yellow even if they are connected to the supply neutral.


    I am a bit sceptical about the arrangement in the OP. Having a neutral coloured green/yellow run outside a SWA armour with one inside is a bit worrying! Running a separate earth with SWA or AWA cables is common practice but they are connected to the earth bar not the neutral.