What earthing arrangement is this?

Former Community Member
Former Community Member
The supply is from a private transformer in a four core cable 3ph + n. The cable armour is earthed and connected to the MET. However there is also a green and yellow cable connected to the neutral terminal at the main isolator going back to a the transformer casing. The transformer is only 5 or 6 metres away. I think this must have been intended to make it a tncs supply but seems to me to just create parallel neutral conductors. Or is it tn-s-c-s?  I have only been able to go off visual inspection because I could not disconnect the supply..
Parents
  • Former Community Member
    0 Former Community Member

    John Peckham:

    Evening OMS


    Not according to BS 7430, GN8 and the ECA Guide to the Wiring Regulations.




     

    Well, with all due respect to the publications author, they are wrong - and there is a certain amount of copying in class going on anyway on this issue


    Your argument is based on nothing more than the length of a conductor connecting to the means of earthing  - ie, if you physically don't make a connection at the TX spill box, and make it at the switchboard then it must be TNC-S - which is complete nonsense.


    If I give you the example of a switchboard with the transformer forming part of the board, your logic says TN-S (because you cannot see the short length of copper from the winding ends to the switchboard neutral)


    If I sperate the switchboard and transformer by a short distance and use a bit of cable to make that link, then your logic says "Ahh - but it's TN-C-S"


    Only if the neutral conductor is connected to earth at the transformer spill box and again at the consumer switchgear (or anywhere along that run) does it become TN-C-S. In most circumstances that would be unusual, because you cannot determine where Earth Fault current is going via the protection CT's - eg, you couldn't operate a Restricted earth fault scheme operating from the star point, including the LV windings and up to the primary circuit breaker


    I suggest you apply the same logic to a generator as you do to the transformer and then tell me it's TN-C-S


    Regards


    OMS


Reply
  • Former Community Member
    0 Former Community Member

    John Peckham:

    Evening OMS


    Not according to BS 7430, GN8 and the ECA Guide to the Wiring Regulations.




     

    Well, with all due respect to the publications author, they are wrong - and there is a certain amount of copying in class going on anyway on this issue


    Your argument is based on nothing more than the length of a conductor connecting to the means of earthing  - ie, if you physically don't make a connection at the TX spill box, and make it at the switchboard then it must be TNC-S - which is complete nonsense.


    If I give you the example of a switchboard with the transformer forming part of the board, your logic says TN-S (because you cannot see the short length of copper from the winding ends to the switchboard neutral)


    If I sperate the switchboard and transformer by a short distance and use a bit of cable to make that link, then your logic says "Ahh - but it's TN-C-S"


    Only if the neutral conductor is connected to earth at the transformer spill box and again at the consumer switchgear (or anywhere along that run) does it become TN-C-S. In most circumstances that would be unusual, because you cannot determine where Earth Fault current is going via the protection CT's - eg, you couldn't operate a Restricted earth fault scheme operating from the star point, including the LV windings and up to the primary circuit breaker


    I suggest you apply the same logic to a generator as you do to the transformer and then tell me it's TN-C-S


    Regards


    OMS