What earthing arrangement is this?

Former Community Member
Former Community Member
The supply is from a private transformer in a four core cable 3ph + n. The cable armour is earthed and connected to the MET. However there is also a green and yellow cable connected to the neutral terminal at the main isolator going back to a the transformer casing. The transformer is only 5 or 6 metres away. I think this must have been intended to make it a tncs supply but seems to me to just create parallel neutral conductors. Or is it tn-s-c-s?  I have only been able to go off visual inspection because I could not disconnect the supply..
Parents

  • The BS7671 definition of PEN is simply about sharing protective and neutral conductor functions; and the definition of protective conductor functions includes connecting an earth electrode to a source neutral point.



    In my copy of BS 7671 it seems to be worded slightly differently - mentioning only "The earthed point of the source, or an artificial neutral".


    Thus the neutral (star point) of the source could be distinct from the earthed point of the source.


    So in my diagram:
    cb4f0ba7a2819e2221fe9e9b04dd0042-huge-tn-s-paths_zpsyci5uu0c.png


    it doesn't matter how long the conductor between the star point ("0") and the N-PE link is - it's still just a neutral conductor.


    Personally I prefer to think of protective conductors in term of the path of the consumer's connection to Earth - rather than the Earth Fault Loop - as the latter includes the conductors back to the star point - which seems to cause more than its fair share of confusion.


       - Andy,
Reply

  • The BS7671 definition of PEN is simply about sharing protective and neutral conductor functions; and the definition of protective conductor functions includes connecting an earth electrode to a source neutral point.



    In my copy of BS 7671 it seems to be worded slightly differently - mentioning only "The earthed point of the source, or an artificial neutral".


    Thus the neutral (star point) of the source could be distinct from the earthed point of the source.


    So in my diagram:
    cb4f0ba7a2819e2221fe9e9b04dd0042-huge-tn-s-paths_zpsyci5uu0c.png


    it doesn't matter how long the conductor between the star point ("0") and the N-PE link is - it's still just a neutral conductor.


    Personally I prefer to think of protective conductors in term of the path of the consumer's connection to Earth - rather than the Earth Fault Loop - as the latter includes the conductors back to the star point - which seems to cause more than its fair share of confusion.


       - Andy,