This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

What earthing arrangement is this?

Former Community Member
Former Community Member
The supply is from a private transformer in a four core cable 3ph + n. The cable armour is earthed and connected to the MET. However there is also a green and yellow cable connected to the neutral terminal at the main isolator going back to a the transformer casing. The transformer is only 5 or 6 metres away. I think this must have been intended to make it a tncs supply but seems to me to just create parallel neutral conductors. Or is it tn-s-c-s?  I have only been able to go off visual inspection because I could not disconnect the supply..
Parents

  • Could the OP tell us how the cable and green/yellow are connected at the transformer end of the cable?



    OP said the transformer casing - which I guess would mean the HV earth - hence a combined LV/HV earthing arrangement (cold site in old money).


       - Andy.
Reply

  • Could the OP tell us how the cable and green/yellow are connected at the transformer end of the cable?



    OP said the transformer casing - which I guess would mean the HV earth - hence a combined LV/HV earthing arrangement (cold site in old money).


       - Andy.
Children
No Data