John Peckham:
I feel sure that my brief explanation will be disagreed with but my reference sources are BS 7430 and IET Guidance Note 8. GN8 has very clear drawings of the different earthing systems.
If Kirsty asked me if I could only take one GN to my desert island which one would it be I would say GN8. My luxury would be Kirsty herself, just of course for the convivial conversation to while away the time!
OMS:
I agree that the cable connecting the system neutral bar to the case of the transformer sounds really suspect, however
"The transformer tank and associated HV metalwork shall be connected to the HV earth electrode." If there is a combined HV/LV earth electrode, that might explain things, but is it allowed?
Nathaniel:
. . . If the neutral point is the point where the three phases' neutral-ends meet (in or on the transformer), then the conductor in question in PNB is a PEN by this definition. Here, again, this would not have been my choice when thinking about the effects of a break in this conductor with no other fault in the system. Even a TT system could by this definition have a 'PEN conductor' if the neutral from the source runs as a wire to the first earth electrode and then on to the customers, as is often found in overhead supplies with separate HV/LV earthing where the LV earth is at the "next pole". . .
Nathaniel:
If the neutral point is the point where the three phases' neutral-ends meet (in or on the transformer), then the conductor in question in PNB is a PEN by this definition. Here, again, this would not have been my choice when thinking about the effects of a break in this conductor with no other fault in the system.
OMS No it's not - by any definition it would need to be carrying load or imbalance current and earth fault current