Gas pipe insert

This extract from ER G12/issue 4 Amd 12015. Is it common practice for a gas pipe to have a insulated insert? Certainly not here.

5.2 Earthing terminal

5.2.1 Provision of earth terminal

PME earth terminals can be offered to consumers unless there are reasonable grounds to believe either:

- their earthing installation is not designed to BS 7671.

- or

- the type of installation is not suitable for PME. (See Section 6 for examples where it may not be possible to provide a PME earth terminal).

Where a metallic gas service is provided to a consumer’s premises with a PME earth terminal, an insulated insert should be fitted in the gas service.
Parents
  • In domestic properties the steel pipe is not actually removed, but cut through out in the street then the new plastic pipe pushed through it into the house, so you end up with possibly 6’-7’ of “earthy” pipe stuck up in the garage or somewhere, but it is not actually continuous all the way up the street.


    But then there’s a insulating insert at the meter.


    Andy B.
Reply
  • In domestic properties the steel pipe is not actually removed, but cut through out in the street then the new plastic pipe pushed through it into the house, so you end up with possibly 6’-7’ of “earthy” pipe stuck up in the garage or somewhere, but it is not actually continuous all the way up the street.


    But then there’s a insulating insert at the meter.


    Andy B.