This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Voltage drop in building networks

The recent posts about building networks has got me thinking - is there any recommendation for maximum permitted voltage drop within building networks?


Generally the DNO are allowed their +10/-6% variation and then BS 7671 generally allows 5% (or 3%) drop within the consumer's installation - and seemingly most ordinary appliances seemed to be based on a total of those - which is fine where the consumer's installation is directly connected to the DNO's system. But what about when there's maybe many tens of metres of extra cable involved courtesy of a BNO?


I guess that in the old days, when the distributor had responsibility all the way to the meter (so including the BNO as we'd now call it where the meter is at the consumer's end) the ESQCR limits would have applied at the meter terminals so the DNO would have had to designed to a tighter limit at the building's cutout - does anyone know if they still do that?


Otherwise there would seem to need to be some co-ordination between the design of the BNO and the consumer's installation - should the BNO formally 'declare' to the consumer's designer the v.d.? - perhaps as part of the tolerance on nominal voltage?


    - Andy.
Parents
  • Exactly, and in these cases you must remember that an ESI spec transformer still has a secondary voltage of 433V at nominal tap. 


    Regards,


    Alan.
Reply
  • Exactly, and in these cases you must remember that an ESI spec transformer still has a secondary voltage of 433V at nominal tap. 


    Regards,


    Alan.
Children
No Data