Ovens on cooker ccts

In domestic kitchens, what do you think of the practice of connecting ovens to 32/40A cb cooker ccts via dual cooker connection outlet plates? For example, along with a 6kw hob, a 2.5kw oven is connected via a 1.5mm2 3 core h/r flex? One view is that it's acceptable because the flex can't be overloaded and the cb provides s/c protection for the flex, nor would it be coded on an eicr.


F
Parents
  • Former Community Member
    0 Former Community Member
    So we've got this "war zone" where the EICR guy says "not mine sunshine" and the PAT guy says "it hasn't got a plug on it, so how do I test it?" 


    As per the extract I posted above, it is PAT, just the same as all the "hard wired" hand dryers etc you see.......


    Regards


    BOD
Reply
  • Former Community Member
    0 Former Community Member
    So we've got this "war zone" where the EICR guy says "not mine sunshine" and the PAT guy says "it hasn't got a plug on it, so how do I test it?" 


    As per the extract I posted above, it is PAT, just the same as all the "hard wired" hand dryers etc you see.......


    Regards


    BOD