Guys,


BS7671:2018 is classing cables extra low voltage (ELV) as an operating voltage not exceeding 50Vac or 120V ripple-free dc.


BS7671 goes on to further
categorize ELV cables into SELV, PELV, FELV.


For single core green/yellow insulated equipotential bonding cables lets say originating from an earth bar and bonding some structural steel work, are these classed as FELV under BS7671:2018 ?
Parents

  • Mike M:

    Andy thanks for the response.


    BS7671:2018 states


    "Voltage, nominal. Voltage by which an installation (or part of an installation) is designated. The following ranges

    of nominal voltage (rms values for AC) are defined:"

    – Extra-low. Not exceeding 50 V AC or 120 V ripple-free DC, whether between conductors or to Earth.

    – Low. Exceeding extra-low voltage but not exceeding 1000 V AC or 1500 V DC between conductors, or

    600 V AC or 900 V DC between conductors and Earth.

    – High. Normally exceeding low voltage.


    For the protective conductor not to be categorized into one of these groups it would mean that the protective conductor is not part of a system that has a designated nominated voltage. If that is the case then I agree however I am unable to find something to back this up in BS7671, perhaps this is further defined somewhere else ?




    The protective conductor is designed for the highest voltage and fault current that it is anticipated it will have to deal with, so what is the answer to your question?


     

Reply

  • Mike M:

    Andy thanks for the response.


    BS7671:2018 states


    "Voltage, nominal. Voltage by which an installation (or part of an installation) is designated. The following ranges

    of nominal voltage (rms values for AC) are defined:"

    – Extra-low. Not exceeding 50 V AC or 120 V ripple-free DC, whether between conductors or to Earth.

    – Low. Exceeding extra-low voltage but not exceeding 1000 V AC or 1500 V DC between conductors, or

    600 V AC or 900 V DC between conductors and Earth.

    – High. Normally exceeding low voltage.


    For the protective conductor not to be categorized into one of these groups it would mean that the protective conductor is not part of a system that has a designated nominated voltage. If that is the case then I agree however I am unable to find something to back this up in BS7671, perhaps this is further defined somewhere else ?




    The protective conductor is designed for the highest voltage and fault current that it is anticipated it will have to deal with, so what is the answer to your question?


     