BS7671:2018 states
"Voltage, nominal. Voltage by which an installation (or part of an installation) is designated. The following ranges
of nominal voltage (rms values for AC) are defined:"
– Extra-low. Not exceeding 50 V AC or 120 V ripple-free DC, whether between conductors or to Earth.
– Low. Exceeding extra-low voltage but not exceeding 1000 V AC or 1500 V DC between conductors, or
600 V AC or 900 V DC between conductors and Earth.
– High. Normally exceeding low voltage.
For the protective conductor not to be categorized into one of these groups it would mean that the protective conductor is not part of a system that has a designated nominated voltage. If that is the case then I agree however I am unable to find something to back this up in BS7671, perhaps this is further defined somewhere else ?
Mike M:
Andy thanks for the response.
BS7671:2018 states
"Voltage, nominal. Voltage by which an installation (or part of an installation) is designated. The following ranges
of nominal voltage (rms values for AC) are defined:"
– Extra-low. Not exceeding 50 V AC or 120 V ripple-free DC, whether between conductors or to Earth.
– Low. Exceeding extra-low voltage but not exceeding 1000 V AC or 1500 V DC between conductors, or
600 V AC or 900 V DC between conductors and Earth.
– High. Normally exceeding low voltage.
For the protective conductor not to be categorized into one of these groups it would mean that the protective conductor is not part of a system that has a designated nominated voltage. If that is the case then I agree however I am unable to find something to back this up in BS7671, perhaps this is further defined somewhere else ?
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site