Guys,
BS7671:2018 is classing cables extra low voltage (ELV) as an operating voltage not exceeding 50Vac or 120V ripple-free dc.
BS7671 goes on to further categorize ELV cables into SELV, PELV, FELV.
For single core green/yellow insulated equipotential bonding cables lets say originating from an earth bar and bonding some structural steel work, are these classed as FELV under BS7671:2018 ?
Rules and Guidelines
Want to participate in the discussions? Please read our Community Rules and Guidelines. Need some help? Visit Support and Answers.
- State Not Answered
- Locked Locked
- Replies 52 replies
- Subscribers 31 subscribers
- Views 12166 views
- Users 0 members are here
Options
You may also be interested in
This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion
Parents
-
Mike
Andy in my opinion I would agree and I would say the current is the relevant factor. For example we frequently use a 10mm2 bare un-insulated aluminium cable/tape under BS EN/IEC 62305 to conduct millions of volts safely to ground during a strike.
I thought BS EN 62305 indicated that aluminium components of a LPS should be a minimum of 50mm2 if solid round or stranded round and 70mm2 if tape.
Did you mean 10mm diameter (allowable as a reduction for short air terminations) or exceeding the nominal 8mm diameter of circular aluminium of 50mm2 CSA
Regards
OMS
-
Mike
Andy in my opinion I would agree and I would say the current is the relevant factor. For example we frequently use a 10mm2 bare un-insulated aluminium cable/tape under BS EN/IEC 62305 to conduct millions of volts safely to ground during a strike.
I thought BS EN 62305 indicated that aluminium components of a LPS should be a minimum of 50mm2 if solid round or stranded round and 70mm2 if tape.
Did you mean 10mm diameter (allowable as a reduction for short air terminations) or exceeding the nominal 8mm diameter of circular aluminium of 50mm2 CSA