Gas Pipes.

Greetings all,

 why does reg. 543.2.3 prohibit the use of a gas pipe as a protective conductor? After all it can be main bonded and then carry substantial currents under certain conditions.


Z.
Parents
  • The risk is nil while the pipes remain closed. Nasty things happen, as they have to plumbers as well, when a fitting or union is loosened to change a meter or an ECV and current was flowing.

    There is at least one case of a plumber being killed while removing a stopcock in a supply pipe outdoors, as he unwittingly also interrupted the neutral return for quite a lot of load at the same time. With gas far smaller currents could still pose an ignition hazard during disconnection if a spark can be drawn.

    Insulating joints (IJs)  are supposed to be the fix for that, but are rarely seen.
Reply
  • The risk is nil while the pipes remain closed. Nasty things happen, as they have to plumbers as well, when a fitting or union is loosened to change a meter or an ECV and current was flowing.

    There is at least one case of a plumber being killed while removing a stopcock in a supply pipe outdoors, as he unwittingly also interrupted the neutral return for quite a lot of load at the same time. With gas far smaller currents could still pose an ignition hazard during disconnection if a spark can be drawn.

    Insulating joints (IJs)  are supposed to be the fix for that, but are rarely seen.