broadgage:
Contrary to a widely held belief, an RCD still gives some protection on systems with no CPC or on systems with neither of the supply wires earthed. (as with many inverters and small generators)
Most dangerous electric shocks are a result of current passing through the body from a live conductor to the general mass of earth or to articles connected thereto. Any current through the body of the victim is not returning to the source via the other circuit conductor, and would therefore operate an RCD regardless of what if any earthing arrangements exist.
ebee:
broadgage:
Contrary to a widely held belief, an RCD still gives some protection on systems with no CPC or on systems with neither of the supply wires earthed. (as with many inverters and small generators)
Most dangerous electric shocks are a result of current passing through the body from a live conductor to the general mass of earth or to articles connected thereto. Any current through the body of the victim is not returning to the source via the other circuit conductor, and would therefore operate an RCD regardless of what if any earthing arrangements exist."systems with neither of the supply wires earthed" Have I misunderstood that bit? Yes without a cpc you`d still get an RCD to work for earth fault protection but if neither of the supply wires were earth referenced the RCD would not trip on earth fault, there would be no earth path therefore no danger , example bathroom shaver socket or isolating transformer
one side of the supply is inadvertently earthed, perhaps by cumulative leakage currents, or by a pre-existing earth fault. In this case a dangerous current could pass through the victim, perhaps with fatal results. A working RCD will trip and avoid this danger.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site