The regs for caravans and mobile transportable units say to earth/bond exposed conductive parts via the MET however I don't have a 240V system and therefore no MET. Providing an earth electrode seemed the best answer.
davezawadi:
This is correct Alan. This stuff Broadgauge seems to be putting out is simply incorrect. If he decides to draw himself a circuit he will see precisely why. RCDs are not a universal panacea for all known faults and possible dangers!
Nathaniel:
If the system is just 'safe' voltage, e.g. 12 V, then there's simply no point considering any earthing for safety reasons. In that case the only point in 'earthing' is in the sense of the word commonly used for vehicles, meaning connecting to the metal chassis (not the actual earth) in order to use that as a conductor in the circuit to save on wires. If you're happy to use separate wires for the whole circuit (not the chassis), you'd probably be better to leave the whole 12 V system isolated from the vehicle and earth.
It's only if there's a source of dangerous voltage involved (e.g. external hookup or internal inverter) that there's any reason to consider connections to the chassis (other than the functional reason above) or to the actual earth. In the case that the dangerous voltage is from an internal source and no part of the wiring will leave the vehicle (fixed internal load), there's no point in connections from the vehicle to the actual earth.