Earth Leakage Measurements
Hi.
I got hold of an earth leakage clamp and took it home to my flat to measure things as a matter of interest after using it at work.
I got some strange readings though.
I made a breakout plug and socket with the lead connecting them having the earth wire taken outside the sheath so that I can clamp onto just the line and neutral. Whatever I got on the line/neutral I also got on the earth so at least that was consistent.
It was interesting to note that there is quite a bit of circulating current flowing through all the pipework. I measured 5mA at one of the radiators. Even with the main switch off there was 2mA.
Anyway, the following readings were taken first from the items of equipment, then from the CU tails. The earthing conductor was slightly different so I didn't take the reading from there as there would be parallel earth paths, so more accurate from the tails.
3kW kettle. 0.03mA   Tails 4mA
Martindale  7mA        Tails 4mA
2 core flex of pendant with retrofit LED lamp. 0mA    Tails 0.05mA
I was expecting that maybe there would be some very slight difference but not this much.
The one at the light fitting is confusing as there is no earth connection. All I can theorise is that the current flow is setting up an earth leakage in the installation wiring. But that is not consistent with the other 2 readings as the kettle is so much higher and the Martindale the opposite way round. I also expected to see a much higher reading taken at the kettle itself as it has an MI heating element known for it's high leakage.
Anyone have any thoughts on this?
  • Sparky
    i have a number of earth leakage clapmeters more than is healthy for one person.
    I have a standing earth leakage when clamping my tails of 11mA plus or minus a couple of mA when measured with a few of my meters. If you just clamp the earthing conductor or a bonding conductor you can measure a good few mA. Or maybe As. This is due to network circulating currents making their way back to the transformer via parallel paths.
    You will be able small leakages due to capacitive leakages to earth from live conductors run in earthed Wiring containment or in close proximity to a cpc.
  • Clapmeters? is that not the same type of device that Hughie Green used to have on the TV prog Opportunity Knocks a few years back?
  • That was a clapometer! Very effective for STDs.
  • Well spotted gentlemen. Clearly that should have read clampmeter.
  • John, you were waiting to see which one of us would spot that one (Known as the "Captain Mainwaring Defence") ?