Derating factors for Cable trays with cover
“Ampacity of cables in covered tray" developed by Engmann  concluded that the ampacities of cables in ventilated trays with cover are 70% to 75% of the open-top tray ampacities .
I can't find such derating factors in BS 7671 neither in IEC 60364-5-52. Please clarify.
    They aren't published in BS 7671 - and there are a variety of methods of lidding including ventilated and unventilated  - which perhaps explains why
    Whilst ampacity reduction to 75% is fairly normal, when tested, it's often less as the flat steel cover is quite a good radiant emitter
    I don't think you'll find definitive published derating factors, this is very much one for the engineer to make a judgement
    OMS
  • If you cable is over 50m then it is probably sized on volt drop and the derating may not matter.
    And if the cover is there to provide shade from the sun, it may be helping the rating factors.