AJJewsbury:
So in my example of plastic conduit and plastic switch and box coming from a steel trunking, it is actually a two gang switch on two different circuits, it is acceptable to have (in this example) just a live and switch live for each circuit down to the switch but an earth isn’t required as regards eddy current considerations as there can be no possibility of an earth fault at the switch due to its plastic construction?
That's about the size of it!
Please see 411.3.1.1
I'd suggest otherwise.
If it's an all-insulated switch then protection against electric shock is by double or reinforced insulation rather than ADS (how could ADS operate without any earthed metalwork?) Thus it's not section 411 that applies but 412. It's therefore the (not greatly dissimilar) regulation 412.2.3.2 we should be looking at. 412.2.3.2 does have a get-out though (via 412.1.2) where the system is controlled so that unauthorised changes (such as the introduction of class I accessories) can't be made.
- Andy.
AJJewsbury:
So in my example of plastic conduit and plastic switch and box coming from a steel trunking, it is actually a two gang switch on two different circuits, it is acceptable to have (in this example) just a live and switch live for each circuit down to the switch but an earth isn’t required as regards eddy current considerations as there can be no possibility of an earth fault at the switch due to its plastic construction?
That's about the size of it!
Please see 411.3.1.1
I'd suggest otherwise.
If it's an all-insulated switch then protection against electric shock is by double or reinforced insulation rather than ADS (how could ADS operate without any earthed metalwork?) Thus it's not section 411 that applies but 412. It's therefore the (not greatly dissimilar) regulation 412.2.3.2 we should be looking at. 412.2.3.2 does have a get-out though (via 412.1.2) where the system is controlled so that unauthorised changes (such as the introduction of class I accessories) can't be made.
- Andy.