Tracing an underground cable fault?

Has anyone any experience of tracing an underground cable fault?

The cable supplies a private estates street lighting.

It's a 3 core 4mm SWA, approx. 50 metres in length, it has a Line to Earth fault.

I haven't separated the armour and internal earth core, so it could be a armour to Line cable fault, or a CPC to LIne fault. Either way the cable needs to be repaired.

We do not have drawings of where it runs, and from a site survey, it isnt obvious how it has been run either, logic would suggest it runs under the pavement, but a test digging yesterday at the first lamppost suggests it runs a direct route to its source across a garden.

I tested at both ends yesterday, it gave a wandering ~1600 ohms L-E reading, I was hoping the reading would be steady, then I could estimate where the fault was with the differing resisitance values from each end, but the reading was not steady at all - water ingress?

I did zap it a few times at 1000V insulation test, this made no difference, and, of course, gave a 0.00 Mohm reading.


Are there Companies with the equipment that is capable of tracing these faults?

We really don't want to dig up 50 metres of tarmaced pavement.
Parents
  • Reminds me years ago my dad was making holes for a new fence at the school were he worked and one of the boys from the school came to ask my dad why none of the lights in the school were working  turns out he'd gone through a 3 phase cable that supplied a group of the port classrooms that were more or less permenant the thing was my dad didn't here a bang or even feel a tingle despite making the holes with an iron bar
Reply
  • Reminds me years ago my dad was making holes for a new fence at the school were he worked and one of the boys from the school came to ask my dad why none of the lights in the school were working  turns out he'd gone through a 3 phase cable that supplied a group of the port classrooms that were more or less permenant the thing was my dad didn't here a bang or even feel a tingle despite making the holes with an iron bar