Tracing an underground cable fault?

Has anyone any experience of tracing an underground cable fault?

The cable supplies a private estates street lighting.

It's a 3 core 4mm SWA, approx. 50 metres in length, it has a Line to Earth fault.

I haven't separated the armour and internal earth core, so it could be a armour to Line cable fault, or a CPC to LIne fault. Either way the cable needs to be repaired.

We do not have drawings of where it runs, and from a site survey, it isnt obvious how it has been run either, logic would suggest it runs under the pavement, but a test digging yesterday at the first lamppost suggests it runs a direct route to its source across a garden.

I tested at both ends yesterday, it gave a wandering ~1600 ohms L-E reading, I was hoping the reading would be steady, then I could estimate where the fault was with the differing resisitance values from each end, but the reading was not steady at all - water ingress?

I did zap it a few times at 1000V insulation test, this made no difference, and, of course, gave a 0.00 Mohm reading.


Are there Companies with the equipment that is capable of tracing these faults?

We really don't want to dig up 50 metres of tarmaced pavement.
Parents
  • I had just this problem many years ago in a 3rd world country. The fault was intermittent which I solved by putting 2 electrodes in a bath of slightly salty water in series so that the fault kept occurring but the breaker didn't trip.

    Once I had a decent short circuit, I fed a known current down the cable to the fault and used the remaining length of the faulty core and a good core connected in series as a voltmeter lead to measure the volt drop from source to fault.

    This gave a remarkably accurate location which turned out to be in a duct under a road so it must have been a manufacturing fault.
Reply
  • I had just this problem many years ago in a 3rd world country. The fault was intermittent which I solved by putting 2 electrodes in a bath of slightly salty water in series so that the fault kept occurring but the breaker didn't trip.

    Once I had a decent short circuit, I fed a known current down the cable to the fault and used the remaining length of the faulty core and a good core connected in series as a voltmeter lead to measure the volt drop from source to fault.

    This gave a remarkably accurate location which turned out to be in a duct under a road so it must have been a manufacturing fault.