Minimum values of insulation resistance

What is the science behind the 1 MOhm minimum insulation resistance? What is the basis for this particular value?
Parents

  • Zoomup:




    Wombat:

    What is the science behind the 1 MOhm minimum insulation resistance? What is the basis for this particular value?




    The value was chosen because it is a nice round figure and easily remembered. 98759.3k Ohms just would not do. It was set to limit current leakage to safe levels and not waste electricity. In fact in the 14th edition wiring regs. fixed wiring was to have an insulation resistance of at least 1 Meg Ohm, but disconnected apparatus could have a minimum insulation resistance of 0.5 MegOhms if the apparatus had no British Standard. Actually our "modern" regs some years ago also specified just a 0.5MegOhm value. (16th Edition, 2001, Table 71A.


    Z.


     




    Thank you for this comment. Where you mentioned "It was set to limit current leakage to safe levels.." What was the criteria for determining the safe level?


    Referring to  IEC/TR 61200-413, a touch voltage of 50V can be sustained by a person indefinitely. (dry conditions) Using an average body resistance of 2000 Ohms gives a current of 25 mA.ac


    Referring to IEC/TR 60479-1 25 mA is in the AC-3 region
    Strong involuntary muscular contractions. Difficulty in breathing. Reversible

    disturbances of heart function. Immobilization may occur. Effects increasing

    with current magnitude. Usually no organic damage to be expected


    So that is considered acceptable and presumably the rationale behind the 30mA RCD


    If we go to the parallel DC curves in the DC-2 region which is less hazardous than the DC-3
    Involuntary muscular contractions likely especially when making, breaking

    or rapidly altering current flow but usually no harmful electrical

    physiological effects


    And we use say 25mA dc to parallel the 25mA ac.


    With a 500V DC Megger and a 25mA leakage current we get 20000 Ohms insulation resistance.


    So the numbers do not stack up on what is considered safe.


     

Reply

  • Zoomup:




    Wombat:

    What is the science behind the 1 MOhm minimum insulation resistance? What is the basis for this particular value?




    The value was chosen because it is a nice round figure and easily remembered. 98759.3k Ohms just would not do. It was set to limit current leakage to safe levels and not waste electricity. In fact in the 14th edition wiring regs. fixed wiring was to have an insulation resistance of at least 1 Meg Ohm, but disconnected apparatus could have a minimum insulation resistance of 0.5 MegOhms if the apparatus had no British Standard. Actually our "modern" regs some years ago also specified just a 0.5MegOhm value. (16th Edition, 2001, Table 71A.


    Z.


     




    Thank you for this comment. Where you mentioned "It was set to limit current leakage to safe levels.." What was the criteria for determining the safe level?


    Referring to  IEC/TR 61200-413, a touch voltage of 50V can be sustained by a person indefinitely. (dry conditions) Using an average body resistance of 2000 Ohms gives a current of 25 mA.ac


    Referring to IEC/TR 60479-1 25 mA is in the AC-3 region
    Strong involuntary muscular contractions. Difficulty in breathing. Reversible

    disturbances of heart function. Immobilization may occur. Effects increasing

    with current magnitude. Usually no organic damage to be expected


    So that is considered acceptable and presumably the rationale behind the 30mA RCD


    If we go to the parallel DC curves in the DC-2 region which is less hazardous than the DC-3
    Involuntary muscular contractions likely especially when making, breaking

    or rapidly altering current flow but usually no harmful electrical

    physiological effects


    And we use say 25mA dc to parallel the 25mA ac.


    With a 500V DC Megger and a 25mA leakage current we get 20000 Ohms insulation resistance.


    So the numbers do not stack up on what is considered safe.


     