Minimum values of insulation resistance

What is the science behind the 1 MOhm minimum insulation resistance? What is the basis for this particular value?
Parents

  • Wombat:




    Zoomup:

    Why was one MegOhm chosen?


    For equipment rated above 1000 volts the one MegOhm rule is usually stated as a minimum of one MegOhm per thousand volts. Although this rule is somewhat arbitrary, and may be criticised as lacking an engineering foundation, it has stood the test of a good many years of practical experience. It gives some assurance that equipment is not too wet or dirty and has saved many an unnecessary breakdown. More recent studies of the problem, however, have resulted in formulas for minimum values of insulation resistance that are based on the kind of insulating material used and the electrical and physical dimensions of the types of equipment under consideration.


    Z.




    Can you provide any references to these studies for XLPE and PVC insulated cables please?


     




    Please read in an old style Dickensian London accent....


    Sorry Mr. Wombat Sir, I is only a 'umble simple sparks and mainly nicks 'is information from hothers. I is evva so 'umble and simple so please hexcuse me not bein' able to offer any haditional hinformation to this matter. So sorry. Please hexcuse me.


    Your obedient servant,


    Z.

Reply

  • Wombat:




    Zoomup:

    Why was one MegOhm chosen?


    For equipment rated above 1000 volts the one MegOhm rule is usually stated as a minimum of one MegOhm per thousand volts. Although this rule is somewhat arbitrary, and may be criticised as lacking an engineering foundation, it has stood the test of a good many years of practical experience. It gives some assurance that equipment is not too wet or dirty and has saved many an unnecessary breakdown. More recent studies of the problem, however, have resulted in formulas for minimum values of insulation resistance that are based on the kind of insulating material used and the electrical and physical dimensions of the types of equipment under consideration.


    Z.




    Can you provide any references to these studies for XLPE and PVC insulated cables please?


     




    Please read in an old style Dickensian London accent....


    Sorry Mr. Wombat Sir, I is only a 'umble simple sparks and mainly nicks 'is information from hothers. I is evva so 'umble and simple so please hexcuse me not bein' able to offer any haditional hinformation to this matter. So sorry. Please hexcuse me.


    Your obedient servant,


    Z.