Therefore each circuit can pass an insulation test, but the whole board can fail, so what do you do next?
AJJewsbury:
But there is no BS 7671 value for a single circuit to pass/fail - just one for the complete DB's worth - 1MΩ*
If the whole DB fails, then it's a fail.
* for initial verification at least.
AJJewsbury:
Regulation 643.2 says nothing about DBs
It's implied - given 314.4 you've got to have a DB between the distribution circuit and the final circuits (OK I could have been clearer that it includes the sub-main as well as the DB and final circuits).
mapj1:
Is an NE fault immedately dangerous, potentially dangerous, or just extremely annoying if it causes nuisance tripping ?
Personally, I think without another fault, such as an open CPC - which may come with the cable damage (rings are nice as you can test for that) or LN reversal, it is probably more of a pain than an immediate danger.
mapj1:
I think those are 'potential' dangers. Diverted neutral currents flow up every water and gas pipe in some streets, without injury, as the DNOs do not distinguish between N and E, and in other parts of the world an NE bond would be permitted and in some cases required by regulation .
mapj1:
I'm not saying an NE short is a good thing - far from it, but If all it does is lower R2 or trip an RCD prematurely above some modest level of load, then is only being a pain to the user, not the same 'immediate ' danger comparable to exposed live parts.
I don't think RCD tripping prematurely is the only outcome. RCD not tripping at all is another possibility (but perhaps not too common thankfully).
Only a really badly designed system becomes dangerous in a power cut and I'd hope they have back up power or some pre-arranged back-up supply.
And as noted above, when we started putting RCDs in, quite a lot of dormant N-E faults were found and had to be fixed, suggesting they had been around a while.
gkenyon:
Wombat:
What is the science behind the 1 MOhm minimum insulation resistance? What is the basis for this particular value?It matches perfectly the permitted touch current for double insulated appliances (0.5 mA) for a supply voltage U0 of 500 V.
For U0 = 1000 V, 1 MΩ would lead to a touch current of 1 mA (the accepted threshold of perception).
These values align with Clause 5.2.7 in BS EN 61140 Protection against electric shock - common aspects for installation and equipment, which states the limit of steady-state touch current to be 0.5 mA AC or 2 mA DC (higher levels are permitted in some circumstances).
In fact, there is some science behind these values, and they are based on the IEC 60479-series of standards Effect of current on human beings and livestock which is used as a reference standard for developing electrical safety standards - BS EN 61140 is itself based on this series of standards.