EICR code- Cooker switch with a socket outlet lacking RCD protection.

1980's end of terrace house, MEM Memera consumer unit with a RCBO to provide 30 mA RCD protection to the socket ring circuit, but no other circuits have RCD protection and there is not any outdoor sockets at all.


There is a cooker switch incorporating a 13-amp socket outlet, which is the closest socket to the kitchen window and with 1.5 metres of it, this socket does not have 30 mA RCD protection, what EICR code should be applied and why?


Andy Betteridge
Parents
  • Is the kitchen window a credible access to the outside for a lawnmower or car charging lead, and / or is it very near a sink ?

    If there are sockets nearer doors then maybe not.


    Many folk would put C3 for no RCD on sockets, assuming the rest of the ADS system is in order, unless there are also additional factors that raise the risk, only then it might become a C2.

    Presumably it has been working just fine for many years ?
Reply
  • Is the kitchen window a credible access to the outside for a lawnmower or car charging lead, and / or is it very near a sink ?

    If there are sockets nearer doors then maybe not.


    Many folk would put C3 for no RCD on sockets, assuming the rest of the ADS system is in order, unless there are also additional factors that raise the risk, only then it might become a C2.

    Presumably it has been working just fine for many years ?