EICR code- Cooker switch with a socket outlet lacking RCD protection.

1980's end of terrace house, MEM Memera consumer unit with a RCBO to provide 30 mA RCD protection to the socket ring circuit, but no other circuits have RCD protection and there is not any outdoor sockets at all.


There is a cooker switch incorporating a 13-amp socket outlet, which is the closest socket to the kitchen window and with 1.5 metres of it, this socket does not have 30 mA RCD protection, what EICR code should be applied and why?


Andy Betteridge
Parents
  • The rental laws lack clarity, the government doesn’t actually seem to say if an EICR with C3 observations on it is acceptable or not.


    If there are EICRs with issues coded C3 will there have to be a lot of belated improvements and upgrades to electrical installation later this year?


    Andy Betteridge
Reply
  • The rental laws lack clarity, the government doesn’t actually seem to say if an EICR with C3 observations on it is acceptable or not.


    If there are EICRs with issues coded C3 will there have to be a lot of belated improvements and upgrades to electrical installation later this year?