EICR code- Cooker switch with a socket outlet lacking RCD protection.

1980's end of terrace house, MEM Memera consumer unit with a RCBO to provide 30 mA RCD protection to the socket ring circuit, but no other circuits have RCD protection and there is not any outdoor sockets at all.


There is a cooker switch incorporating a 13-amp socket outlet, which is the closest socket to the kitchen window and with 1.5 metres of it, this socket does not have 30 mA RCD protection, what EICR code should be applied and why?


Andy Betteridge
Parents

  • What happens if 99 per cent of it is in good condition, is the whole installation to be condemned as dangerous?



    Yes, but you only have to get 1% fixed to change that.


       - Andy.
Reply

  • What happens if 99 per cent of it is in good condition, is the whole installation to be condemned as dangerous?



    Yes, but you only have to get 1% fixed to change that.


       - Andy.