EICR code- Cooker switch with a socket outlet lacking RCD protection.

1980's end of terrace house, MEM Memera consumer unit with a RCBO to provide 30 mA RCD protection to the socket ring circuit, but no other circuits have RCD protection and there is not any outdoor sockets at all.


There is a cooker switch incorporating a 13-amp socket outlet, which is the closest socket to the kitchen window and with 1.5 metres of it, this socket does not have 30 mA RCD protection, what EICR code should be applied and why?


Andy Betteridge
Parents

  • ebee:
    "that were not done to standard in the first instance"  also where those standards  are now considered considerably lacking in regards to safety



    The standard is the whole process applied during a lifetime. So you EICR a lot of 50 year old + houses that are untouched and "as original"?


    I suppose if you do, who are you gonna call?

     

Reply

  • ebee:
    "that were not done to standard in the first instance"  also where those standards  are now considered considerably lacking in regards to safety



    The standard is the whole process applied during a lifetime. So you EICR a lot of 50 year old + houses that are untouched and "as original"?


    I suppose if you do, who are you gonna call?

     