This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Down light rejected

I came in at a rather late stage in the project where a old office building is being converted into a hotel. The wiring for the lighting was mistakenly routed above the compartment ceilings in the floor void above. The ceilings then had a small number of recessed downlights which were fire rated at 90min. The arrangement has been rejected by Building Control as there is no test evidence for the composite. So be careful when going for similar arrangements! I imagine recent serious fires are beginning to have an impact on the way regulations are interpreted.
Parents
  • I get the drift of what you’re saying, however can you clarify what the composite is?


    I am assuming that with the cables in the void above what is probably fire rated plasterboard, possibly double boarded they and the downlights that are presumably rated less than the ceiling branch the fire protection.


    Andy Betteridge
Reply
  • I get the drift of what you’re saying, however can you clarify what the composite is?


    I am assuming that with the cables in the void above what is probably fire rated plasterboard, possibly double boarded they and the downlights that are presumably rated less than the ceiling branch the fire protection.


    Andy Betteridge
Children
No Data