Caravan electrical hook up?

I've been asked to install a supply to a hook up for a caravan in a garden.

I see that the connection of a PME earthing facility to any metal work is prohibited, is there anything else I may have overlooked?


Thanks in advance :)
Parents
  • Also note that caravan supplies require individual 30mA RCD protection that opens all live poles (including N) - so no relying on a SP RCBO or shared RCCB back at the CU.


    The sockets are now required to be interlocked - beware of the older style hookup boxes or simple BS EN 60309 sockets.


    For underground cables BS 7671 recommends a minimum depth of 600mm in the pitch area unless provided with additional mechanical protection and 6m height for overheads in areas subject to vehicle movement.


    (plus several other pages in section 708)


       - Andy,
Reply
  • Also note that caravan supplies require individual 30mA RCD protection that opens all live poles (including N) - so no relying on a SP RCBO or shared RCCB back at the CU.


    The sockets are now required to be interlocked - beware of the older style hookup boxes or simple BS EN 60309 sockets.


    For underground cables BS 7671 recommends a minimum depth of 600mm in the pitch area unless provided with additional mechanical protection and 6m height for overheads in areas subject to vehicle movement.


    (plus several other pages in section 708)