Obvious departures from the regulations at first glance at a new consumer unit.

I was asked to give an EICR on an domestic property which is to be placed on the market (part P applicable). I found that a builder as part of the other renovation work, (new doors, windows and kitchen etc.) has carried out the installation of a new metal consumer unit. On first opening this dual RCD unit, the 2 lighting circuits were on one R.C.D., and the 2 final ring circuits on the other R.C.D,, it was obvious also, that some wires to the new CB's were short and not lengthened, resulting in a bird's nest at the M.C.B.''s.


Plainly, a qualified electrician hadn't carried out the work. What would the readers as registered electricians have done ?. 1. Walk away. 2. Propose to have an E.I.C.R. carried out (UNSATISFACTORY), then carry out the rectification work and issue MWC's.3. Rectify the obvious departures, issue M.W.C.'s and then issue a SATISFACTORY E.I.C.R. 


Jaymack
Parents
  • This is a real house and an electrician wired the CU as follows:


    RCD 1

    Cooker (32A)

    Kitchen sockets (32A)

    Outside socket (16A)

    Outside lights (6A)


    RCD 2

    Upstairs sockets (32A)

    Downstairs sockets (32A)

    Boiler (16A)

    Inside lights (6A)


    The inside lights circuit was later moved to an RCBO.


     If the cooker switch has a socket you could swap its circuit for the upstairs sockets circuit to leave a working socket in the kitchen if there is a RCD trip, it’s all a bit pedantic.


    Andy Betteridge
Reply
  • This is a real house and an electrician wired the CU as follows:


    RCD 1

    Cooker (32A)

    Kitchen sockets (32A)

    Outside socket (16A)

    Outside lights (6A)


    RCD 2

    Upstairs sockets (32A)

    Downstairs sockets (32A)

    Boiler (16A)

    Inside lights (6A)


    The inside lights circuit was later moved to an RCBO.


     If the cooker switch has a socket you could swap its circuit for the upstairs sockets circuit to leave a working socket in the kitchen if there is a RCD trip, it’s all a bit pedantic.


    Andy Betteridge
Children