Obvious departures from the regulations at first glance at a new consumer unit.

I was asked to give an EICR on an domestic property which is to be placed on the market (part P applicable). I found that a builder as part of the other renovation work, (new doors, windows and kitchen etc.) has carried out the installation of a new metal consumer unit. On first opening this dual RCD unit, the 2 lighting circuits were on one R.C.D., and the 2 final ring circuits on the other R.C.D,, it was obvious also, that some wires to the new CB's were short and not lengthened, resulting in a bird's nest at the M.C.B.''s.


Plainly, a qualified electrician hadn't carried out the work. What would the readers as registered electricians have done ?. 1. Walk away. 2. Propose to have an E.I.C.R. carried out (UNSATISFACTORY), then carry out the rectification work and issue MWC's.3. Rectify the obvious departures, issue M.W.C.'s and then issue a SATISFACTORY E.I.C.R. 


Jaymack
Parents

  • Sparkingchip:



    If the cooker switch has a socket you could swap its circuit for the upstairs sockets circuit to leave a working socket in the kitchen if there is a RCD trip, it’s all a bit pedantic.




    The cooker switch does not have a socket.


    RCD1 is rated at 80A and RCD2 is rated at 63A. The electrician wired up the CU as previously described because he assumes that the upstairs and downstairs ring mains will be lightly loaded most of the time, and heavier current consumption will take place on the cooker and kitchen ring main circuits. The outside socket circuit is an unknown quantity but potentially may convey more current than the boiler consumes.


    The house incomer has an 80A fuse in it.



     

Reply

  • Sparkingchip:



    If the cooker switch has a socket you could swap its circuit for the upstairs sockets circuit to leave a working socket in the kitchen if there is a RCD trip, it’s all a bit pedantic.




    The cooker switch does not have a socket.


    RCD1 is rated at 80A and RCD2 is rated at 63A. The electrician wired up the CU as previously described because he assumes that the upstairs and downstairs ring mains will be lightly loaded most of the time, and heavier current consumption will take place on the cooker and kitchen ring main circuits. The outside socket circuit is an unknown quantity but potentially may convey more current than the boiler consumes.


    The house incomer has an 80A fuse in it.



     