Some years ago I started doing electrical work at a farm, originally the farm buildings and house were both connected to the DNO earth terminal.


I altered it so that the farm buildings are TT , but left the house connected to the DNO earth terminal. The possible issues are that there is a steel clad switch fuse enclosure for the house inside a wooden cupboard in the farm workshop and the SWA cable for the house passes through the ground immediately adjacent to the farm building. But there was no physical connection between the house and farm earthing arrangements.


It had been like that for a few years as the house has not had any alterations at all, just a few repairs. So the house installation is effectively exactly the same as it was when the house and the farm buildings were thirty years ago and connected up as a new installation by the DNO.


However (you knew there was going to be a however!) a couple of years ago PV panels were installed on the farm building roof and the installers used the DNO and house earth terminal rather than the farm buildings earth terminal, despite the PV system being in and on the farm buildings and it having storage batteries that feed back into the both installations as they share a meter; and the storage batteries act as a supply to emergency lighting in the farm buildings when the installation is off-grid.


I am now reviewing the earth arrangements, the house is empty and needs tidying up, thirty two lights need replacing and odd repairs, there won't be any alterations it is just replacing fittings and replacing MCBs in the split load consumer unit with RCBOs to give additional RCD protection in the house. 


I will leave it at that and not express my thoughts, as it will be more interesting to see what your thoughts are rather than trying to get you to consider mine.


Comments please. 


Andy B
Parents
  • The DNO have installed their network rod from their intake in the plastic meter cabinet on the exterior of farm building, as is common practice in rural locations where the transformer serves supplies one consumers installation and that is where the DNO neutral earth link is not at the transformer.


    I have not suggested interfering with the DNO equipment and I am certainly not stupid enough to break the seals on the DNO and remove the cable and transformer earth connection, merely not using the earth terminal supplied by the DNO for use by the consumer to use at the consumers own risk.


    As I said above I was reasonably happy the buildings being TT and the house being connected to the DNO earth terminal, until the PV installers created an interconnection. I am not convinced that disconnecting the house from the DNO earth is justified, the simplest option of all is to just move the PV earth from the house/ DNO MET to the farm buildings TT MET.


    This would not have happened if the house supply did not originate in the farm buildings, but it does so to reiterate the options to avoid having two interconnected earthing systems are: 

    • Reconnect the farm buildings to the DNO earth terminal, so everything is connected to it.

    • Disconnect everything from the DNO earth terminal and make it all TT.

    • Just move the PV and batteries installation earth conductor to the farm buildings TT MET and leave just the house connected to the DNO earth terminal.


    Andy Betteridge
Reply
  • The DNO have installed their network rod from their intake in the plastic meter cabinet on the exterior of farm building, as is common practice in rural locations where the transformer serves supplies one consumers installation and that is where the DNO neutral earth link is not at the transformer.


    I have not suggested interfering with the DNO equipment and I am certainly not stupid enough to break the seals on the DNO and remove the cable and transformer earth connection, merely not using the earth terminal supplied by the DNO for use by the consumer to use at the consumers own risk.


    As I said above I was reasonably happy the buildings being TT and the house being connected to the DNO earth terminal, until the PV installers created an interconnection. I am not convinced that disconnecting the house from the DNO earth is justified, the simplest option of all is to just move the PV earth from the house/ DNO MET to the farm buildings TT MET.


    This would not have happened if the house supply did not originate in the farm buildings, but it does so to reiterate the options to avoid having two interconnected earthing systems are: 

    • Reconnect the farm buildings to the DNO earth terminal, so everything is connected to it.

    • Disconnect everything from the DNO earth terminal and make it all TT.

    • Just move the PV and batteries installation earth conductor to the farm buildings TT MET and leave just the house connected to the DNO earth terminal.