ProMbrooke:More likely around this:
V fault = Vsupply *(Rlive /(Rcpc +Rlive))
230V supply.
- 1.5 sqmm cable has 1.0 sqmm CPC touch voltage on fault becomes 110V
- 2.5 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 95V
- 4 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 88V
- 6 sqmm cable has 2.5 sqmm CPC touch voltage on fault becomes 70V
- 10 sqmm cable has 4 sqmm CPC touch voltage on fault becomes 64V
- 16 sqmm cable has 6 sqmm CPC touch voltage on fault becomes 50V
Yes but ... that only works indoors. And even there, slightly over 70 V is too much for 5 s ... perhaps even 1 s.
What about when you supply equipment outdoors, and have no control over the voltage at a person's feet as you might have within a building (what we used to term "equipotential zone")?
The worst case is a TT system, because the full U0 is available outdoors, and 1 s is way too long.
Next up comes a TN-S system where the installation is some distance from the transformer supplying it.
The actual answer, as Mike alluded to, is that it's an engineering compromise between what's practicable, and the likely risk of shock in a fault condition (larger conductors perhaps less likely to break, often in more robust wiring systems etc.).
ProMbrooke:More likely around this:
V fault = Vsupply *(Rlive /(Rcpc +Rlive))
230V supply.
- 1.5 sqmm cable has 1.0 sqmm CPC touch voltage on fault becomes 110V
- 2.5 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 95V
- 4 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 88V
- 6 sqmm cable has 2.5 sqmm CPC touch voltage on fault becomes 70V
- 10 sqmm cable has 4 sqmm CPC touch voltage on fault becomes 64V
- 16 sqmm cable has 6 sqmm CPC touch voltage on fault becomes 50V
Yes but ... that only works indoors. And even there, slightly over 70 V is too much for 5 s ... perhaps even 1 s.
What about when you supply equipment outdoors, and have no control over the voltage at a person's feet as you might have within a building (what we used to term "equipotential zone")?
The worst case is a TT system, because the full U0 is available outdoors, and 1 s is way too long.
Next up comes a TN-S system where the installation is some distance from the transformer supplying it.
The actual answer, as Mike alluded to, is that it's an engineering compromise between what's practicable, and the likely risk of shock in a fault condition (larger conductors perhaps less likely to break, often in more robust wiring systems etc.).