ProMbrooke:mapj1:
Am I correct to say that even at maximum allowable EFLIs, breakers 100 amps and under will trip in their magnetic region?
Mostly true, and certainly true to say you will get prompt clearance for faults from live to to neutral on circuits that meet the full load voltage drop requirements of Lighting 3% other uses 5% .?
(and that allows us to get an approx figure for the live path of half the L-N loop resistance)
Faults from live to earth need to be considered separately and problems really arise when the earth impedance is significantly higher - for example for a TNS service that is only just meeting the local DNOs spec the earth loop impedance may be as high as 0.8 ohms on a supply with a 100A fuse - so the PSSC to earth is 230/0.8 ~ 285A, but the LN loop may be more like (10V/100A 10 milliohms) 2kA short circuit prospective
Now that may not fire a C type 32A breaker on an earth fault, but it probably will, and it will certainly fire the more common B32 that we use for most socket circuits, if the fault is at or near the consumer unit end.
However a shower on a B50Amp breaker might need as much as 250A to instant trip, and if the external earth resistance is the maximum 0.8 ohms permitted it may or may not do so if the fault is at the remote end of more than about 30m of T and E cable.
Of course in the last few years that MCB would have become a 50A RCBO, but there are a lot in use out there that pre-date that change. (so remove the bathroom bonding in an old house at your peril.. )
M.
In the world of big stuff you may introduce programmed delays of 1sec or 3 sec or 5 sec to give some discrimination with downstream protection, but in practice 5 secs is a long time to be standing in front of something that is growling and smoking because one phase is shorted.
What are the typical real world Ze values being measured in domestics?
Ze in my part of the woods (Norfolk U.K.) for TN-C-S average 0.20/0.30 Ohms.
For TT with an earth rod average 200 Ohms in damp well draining sandy soil.
Z.
ProMbrooke:mapj1:
Am I correct to say that even at maximum allowable EFLIs, breakers 100 amps and under will trip in their magnetic region?
Mostly true, and certainly true to say you will get prompt clearance for faults from live to to neutral on circuits that meet the full load voltage drop requirements of Lighting 3% other uses 5% .?
(and that allows us to get an approx figure for the live path of half the L-N loop resistance)
Faults from live to earth need to be considered separately and problems really arise when the earth impedance is significantly higher - for example for a TNS service that is only just meeting the local DNOs spec the earth loop impedance may be as high as 0.8 ohms on a supply with a 100A fuse - so the PSSC to earth is 230/0.8 ~ 285A, but the LN loop may be more like (10V/100A 10 milliohms) 2kA short circuit prospective
Now that may not fire a C type 32A breaker on an earth fault, but it probably will, and it will certainly fire the more common B32 that we use for most socket circuits, if the fault is at or near the consumer unit end.
However a shower on a B50Amp breaker might need as much as 250A to instant trip, and if the external earth resistance is the maximum 0.8 ohms permitted it may or may not do so if the fault is at the remote end of more than about 30m of T and E cable.
Of course in the last few years that MCB would have become a 50A RCBO, but there are a lot in use out there that pre-date that change. (so remove the bathroom bonding in an old house at your peril.. )
M.
In the world of big stuff you may introduce programmed delays of 1sec or 3 sec or 5 sec to give some discrimination with downstream protection, but in practice 5 secs is a long time to be standing in front of something that is growling and smoking because one phase is shorted.
What are the typical real world Ze values being measured in domestics?
Ze in my part of the woods (Norfolk U.K.) for TN-C-S average 0.20/0.30 Ohms.
For TT with an earth rod average 200 Ohms in damp well draining sandy soil.
Z.