5 second disconnection times

Hi all


Something that I have always wondered about since I started doing electrical work.


The 0.4 and 5 second disconnection times. 0.4 makes sense as it is quick.

However 5 seconds still seems a long time for exposed conductive parts to remain live. When I first started, lighting circuits had a 5s time.

Now it's 0.4 for all circuits feeding socket outlets up to 63A but only for fixed equipment up to 32A. So any equipment over 32A can be 5s.

The reason given in collage was that it was portable equipment that can be picked up and gripped but fixed equipment can be pulled away from.

Previously, in 16th ed regs, the 0.4 was for socket outlets and circuits supplying equipment that can be hand held.

However, 5 seconds still seems a long time for exposed metalwork to be live. I know with a low impedance earth the voltage will be lower, but still.


The other thing is that even a distribution circuit that can have 5s dis time, on an earth fault, say in an armoured cable, all earthed metalwork can be live for the full 5 seconds, even hand held equipment on circuits with a 0.4s dis time. I realise that if the fault was on the actual item of equipment itself the voltage would be higher.


Any equipment, though, above 32A can still have a 5s dis time. I come across fixed equipment all the time that is above 32A. This equipment quite often has parts of it that can actually be gripped. When the body has electricity passing though it the muscles contract so it may be hard to pull away.

I've seen a video of three men pushing a tower hitting an overhead HV line. all three dropped down but their hands still gripped the scaffold poles.

I know were dealing with LV but the muscles still react the same.

Even showers could once have a 5s dis time and the only thing that has changed that is the regs for RCDs in rooms containing a bath or shower. It's still on a circuit that, without the RCD, allows 5s.


The fact that the regs have tightened up of what circuits can have 5s dis times shows that there is still a danger on 5s. Otherwise, why change them to 0.4s.


Any thoughts?



  • Former Community Member
    Former Community Member
    Do you have any specific Hager, Crabtree, Wylex, ect curves? Those are generic more or less at first glance. I'll start reading the thread, looks good :)  


    Right, but truth is most circuits are still tripping on magnetic trip since type B & C breakers are the most commonly used. The nominal voltage might be 230, but most actually still measure 240-250.
  • Do have some time current curves for D types? You're right, but I just want to compare curves.

    The curves as far as I can tell aren't defined by the standard (which only gives times to be met for a few spot currents) - so the curves might vary a bit by manufacturer. They're also complicated by the fact that the standard has different requirements for different ratings of MCB - e.g. 10A & below and above 32A D-types may take 8s to disconnect at 10x whereas all other ratings must disconnect within 4s. Such differences are often glossed over in simple curves that scales in simple multiples of In.


    But here's the curves from ABB for one example: https://library.e.abb.com/public/114371fcc8e0456096db42d614bead67/2CDC400002D0201_view.pdf


    If you want some bedtime reading on the peculiarities of D-types and 5s disconnection times try https://communities.theiet.org/discussions/viewtopic/1037/24502

    How often do these values actually approach 0.68ohms?

    Given all the fuss we had when Uo changed from 240V to 230V and then again when Cmin was introduced there must be a fair percentage of circuits that are close to maximum permitted Zs. The majority will be lower of course, but that's not something we can really rely on.


      - Andy.
  • ProMbrooke:
    mapj1:
    Am I correct to say that even at maximum allowable EFLIs, breakers 100 amps and under will trip in their magnetic region? 


    Mostly true, and certainly true to say you will get prompt clearance for faults from live to to neutral on circuits that meet the full load voltage drop requirements of Lighting 3% other uses 5% .?


    (and that allows us to get an approx  figure for the live path of half the L-N loop resistance)


    Faults from live to earth need to be considered separately and problems really arise when the earth impedance is significantly higher - for example for a TNS service that is only just meeting the local DNOs spec the earth loop impedance may be as high as 0.8 ohms on a supply with a 100A fuse - so the PSSC to earth is 230/0.8 ~ 285A, but the LN loop may be more like (10V/100A 10 milliohms) 2kA short circuit prospective

    Now that may not fire a C type 32A breaker on an earth fault, but it probably will, and it will certainly fire the more common B32 that we use for most socket circuits, if the fault is at or near the consumer unit end.

    However a shower on a B50Amp breaker might need as much as 250A to instant trip, and if the external earth resistance is the maximum 0.8 ohms permitted it may or may not do so if the fault is at the remote end of more than about 30m of T and  E cable.

    Of course in the last few years that MCB  would have become  a 50A RCBO, but there are a lot  in use out there that pre-date that change. (so remove the bathroom bonding in an old house at your peril.. )

    M.


    In the world of big stuff you may introduce programmed delays of 1sec or 3 sec or 5 sec to give some discrimination with downstream protection, but in practice 5 secs is a long time to be standing in front of something that is growling and smoking because one phase is shorted.




     





    What are the typical real world Ze values being measured in domestics?  




    Ze in my part of the woods (Norfolk U.K.) for TN-C-S average 0.20/0.30 Ohms.


    For TT with an earth rod average 200 Ohms in damp well draining sandy soil.


    Z.


  • Former Community Member
    Former Community Member
    mapj1:
    Am I correct to say that even at maximum allowable EFLIs, breakers 100 amps and under will trip in their magnetic region? 


    Mostly true, and certainly true to say you will get prompt clearance for faults from live to to neutral on circuits that meet the full load voltage drop requirements of Lighting 3% other uses 5% .?


    (and that allows us to get an approx  figure for the live path of half the L-N loop resistance)


    Faults from live to earth need to be considered separately and problems really arise when the earth impedance is significantly higher - for example for a TNS service that is only just meeting the local DNOs spec the earth loop impedance may be as high as 0.8 ohms on a supply with a 100A fuse - so the PSSC to earth is 230/0.8 ~ 285A, but the LN loop may be more like (10V/100A 10 milliohms) 2kA short circuit prospective

    Now that may not fire a C type 32A breaker on an earth fault, but it probably will, and it will certainly fire the more common B32 that we use for most socket circuits, if the fault is at or near the consumer unit end.

    However a shower on a B50Amp breaker might need as much as 250A to instant trip, and if the external earth resistance is the maximum 0.8 ohms permitted it may or may not do so if the fault is at the remote end of more than about 30m of T and  E cable.

    Of course in the last few years that MCB  would have become  a 50A RCBO, but there are a lot  in use out there that pre-date that change. (so remove the bathroom bonding in an old house at your peril.. )

    M.


    In the world of big stuff you may introduce programmed delays of 1sec or 3 sec or 5 sec to give some discrimination with downstream protection, but in practice 5 secs is a long time to be standing in front of something that is growling and smoking because one phase is shorted.




     





    What are the typical real world Ze values being measured in domestics?  


  • Former Community Member
    Former Community Member



    AJJewsbury:
    Am I correct to say that even at maximum allowable EFLIs, breakers 100 amps and under will trip in their magnetic region?

    Not entirely - BS 7671 allows higher EFLIs for D types - e.g. 0.68Ω (table 41.3) for a D32 for 5s disconnection time - so minimum fault current of around 338A  - yet 20xIn (640A) is needed to ensure magnetic operation.

     
    A 60 amp circuit still going to tax the source.

    Not much I would have thought - Max Zs for a 63A BS 88-3 fuse is 0.68Ω for 5s disconnection time - so again minimum fault current of 300-odd amps. Given that most public supply transformers in urban areas are rated at 400A or more per phase, in unfavourable conditions it wouldn't even count as an overload.

      - Andy.





    Do have some time current curves for D types? You're right, but I just want to compare curves.


    How often do these values actually approach 0.68ohms?


  • Am I correct to say that even at maximum allowable EFLIs, breakers 100 amps and under will trip in their magnetic region? 


    Mostly true, and certainly true to say you will get prompt clearance for faults from live to to neutral on circuits that meet the full load voltage drop requirements of Lighting 3% other uses 5% .?


    (and that allows us to get an approx  figure for the live path of half the L-N loop resistance)


    Faults from live to earth need to be considered separately and problems really arise when the earth impedance is significantly higher - for example for a TNS service that is only just meeting the local DNOs spec the earth loop impedance may be as high as 0.8 ohms on a supply with a 100A fuse - so the PSSC to earth is 230/0.8 ~ 285A, but the LN loop may be more like (10V/100A 10 milliohms) 2kA short circuit prospective

    Now that may not fire a C type 32A breaker on an earth fault, but it probably will, and it will certainly fire the more common B32 that we use for most socket circuits, if the fault is at or near the consumer unit end.

    However a shower on a B50Amp breaker might need as much as 250A to instant trip, and if the external earth resistance is the maximum 0.8 ohms permitted it may or may not do so if the fault is at the remote end of more than about 30m of T and  E cable.

    Of course in the last few years that MCB  would have become  a 50A RCBO, but there are a lot  in use out there that pre-date that change. (so remove the bathroom bonding in an old house at your peril.. )

    M.


    In the world of big stuff you may introduce programmed delays of 1sec or 3 sec or 5 sec to give some discrimination with downstream protection, but in practice 5 secs is a long time to be standing in front of something that is growling and smoking because one phase is shorted.




  • Am I correct to say that even at maximum allowable EFLIs, breakers 100 amps and under will trip in their magnetic region?

    Not entirely - BS 7671 allows higher EFLIs for D types - e.g. 0.68Ω (table 41.3) for a D32 for 5s disconnection time - so minimum fault current of around 338A  - yet 20xIn (640A) is needed to ensure magnetic operation.

     
    A 60 amp circuit still going to tax the source.

    Not much I would have thought - Max Zs for a 63A BS 88-3 fuse is 0.68Ω for 5s disconnection time - so again minimum fault current of 300-odd amps. Given that most public supply transformers in urban areas are rated at 400A or more per phase, in unfavourable conditions it wouldn't even count as an overload.

      - Andy.
  • Former Community Member
    Former Community Member
    AJJewsbury:
    Disconnection times (0.4 and 5s) can not be met or achieved via the thermal element in UK/EU MCBs and hence rely on the magnetic (solenoid) trip function. This means that even the max listed EFLI values for type B-D 125 amp MCBs will result in disconnection faster than 0.1 seconds. This leaves us with fuses/devices 125 amps and over which typically have a Zs of <0.25 ohms. Going by ohms law 0.2 gives us 265kw or 1,150 amps with an infinite source.

    .Those sound like rather odd assumptions to me. Many existing UK installations still use fuses for final circuits (either to BS 3036 or what was BS 1361) - anything upwards of 5A - not to mention the ubiquitous 13A fuse in FCUs. While fuses for small final circuits are certainly less fashionable for new work at the moment, they're still permitted so their absence can hardly be a safe assumption for basing disconnection time calculations on. Perhaps more to the point fuses were just about the only option (certainly domestically) when the 5s disconnection time was first introduced - so can't have been the original thinking. Even when MCBs are used for final circuits it's again common practice to use fuses far smaller than 125A for distribution circuits - I have a couple of 63A HBC fuses on distribution circuits at home and even the DNO's fuses are usually between 60A and 100A in the UK so even in that case plausible fault currents are in the region of a few hundred amps rather than thousands.  BTW - it's not quite true that the thermal element of MCBs can't cause the device to open within 5s - it's just that for most cases the current required to do that will trigger the magnetic part first. For some D-type MCBs 5s operation can certainly be achieved using just the thermal element using a lower fault current than needed for magnetic operation (see table 41.3 of BS 7671 for example).


    Also keep in mind that most UK public supplies are tapped to deliver around 250 or 253V at source (to counteract voltage drop in the LV distribution network) - so even with a moderate fault current it's likely there'll still be close to the 230V at the source.


      - Andy.





    True, however look at the time current curves of minature circuit breakers. 0.4 seconds often can not be achieved with typical PFC, so a solenoid coil is added to the breaker. Am I correct to say that even at maximum allowable EFLIs, breakers 100 amps and under will trip in their magnetic region? 


    I am willing to acknowledge that way back when it was assumed the body could tolerate higher touch voltages for much longer periods of time. 


    A 60 amp circuit still going to tax the source.


  • Disconnection times (0.4 and 5s) can not be met or achieved via the thermal element in UK/EU MCBs and hence rely on the magnetic (solenoid) trip function. This means that even the max listed EFLI values for type B-D 125 amp MCBs will result in disconnection faster than 0.1 seconds. This leaves us with fuses/devices 125 amps and over which typically have a Zs of <0.25 ohms. Going by ohms law 0.2 gives us 265kw or 1,150 amps with an infinite source.

    .Those sound like rather odd assumptions to me. Many existing UK installations still use fuses for final circuits (either to BS 3036 or what was BS 1361) - anything upwards of 5A - not to mention the ubiquitous 13A fuse in FCUs. While fuses for small final circuits are certainly less fashionable for new work at the moment, they're still permitted so their absence can hardly be a safe assumption for basing disconnection time calculations on. Perhaps more to the point fuses were just about the only option (certainly domestically) when the 5s disconnection time was first introduced - so can't have been the original thinking. Even when MCBs are used for final circuits it's again common practice to use fuses far smaller than 125A for distribution circuits - I have a couple of 63A HBC fuses on distribution circuits at home and even the DNO's fuses are usually between 60A and 100A in the UK so even in that case plausible fault currents are in the region of a few hundred amps rather than thousands.  BTW - it's not quite true that the thermal element of MCBs can't cause the device to open within 5s - it's just that for most cases the current required to do that will trigger the magnetic part first. For some D-type MCBs 5s operation can certainly be achieved using just the thermal element using a lower fault current than needed for magnetic operation (see table 41.3 of BS 7671 for example).


    Also keep in mind that most UK public supplies are tapped to deliver around 250 or 253V at source (to counteract voltage drop in the LV distribution network) - so even with a moderate fault current it's likely there'll still be close to the 230V at the source.


      - Andy.
  • Former Community Member
    Former Community Member
    mapj1:

    But that factor of 2 in the denominator of your equation 8 should be more like 1.5 in the case of twin and earth. Experience in the rest of Euroland is not so relevant here - in the UK our final circuits do not have full sized CPCs,  (nor do quite a few in-building sub-mains either) and in built up areas we may have larger lower impedance transformers, indeed in parts of London 1MVA transformers are meshed and the LV network in the streets is not even fused (AKA "the solid system"). Then there are a great many tower blocks with a megawatt transformer in the basement, and then bigger office and mixed use buildings with HV going up to a transformer on every 5th floor or so (look at Canary Wharf for an example of that if you like)

    In such cases your assumption that the supply droop has a dominant effect is not appropriate - it is mostly in the cables.

    Note that just because something is written by a committee does not make it infallible - look at the number of times the regs get updated for proof of that. ( I've sat on telecoms standards meetings, I know how it works, and it has perhaps made me slightly cynical. )

    I agree the incoming voltage will droop very significantly during fault for those rural sites fed by smaller (100kVA and down) pole-pig transformers, but they are more commonly earthed as TT anyway.

    I'm not sure we should underestimate the touch voltages to city dwellers by assuming that all installations are like that.

    There is an additional complication in a PME system, as the live voltage goes down the neutral comes up to meet it, so you have to be clear if you mean touch voltag relative to the CPC of the system, or to terra-firma earth voltage either at ground level as on incoming telephone cables etc.

    M.





    I agree, but remember, with MCBs you'll be hitting the instantaneous function even on your maximum permitted Zs. Only larger circuits (over 125 amps) will take time clearing, and those will cause at least some dip even on 1 MVA units. As such I still maintain the the source has a moderate to major effect on touch voltage.


    London like France, New York, Chicago ect are exceptions though. These networks, in particular Con Edison's networks, can be regarded as being almost truly infinite. Evidenced by 500MCM (253mm2) cables burning clear in manholes with only mild, local dimming of lights. At the same time remote earth becomes far more scarce- sidewalks, poor conductive floors, bonded pipes and building steal all work to reduce touch voltage. The scenario of being outside on damp ground while holding a metal tool or electric grill in the back yard like out in the country become very slim. 


    I will agree with you that technical committees get it wrong or in the case of today influenced by the manufacturers, however I still hold the belief that 5 seconds is unlikely to present a danger in most cases.