230V supply.
- 1.5 sqmm cable has 1.0 sqmm CPC touch voltage on fault becomes 138
- 2.5 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 144V
- 4 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 167V
- 6 sqmm cable has 2.5 sqmm CPC touch voltage on fault becomes 162V
- 10 sqmm cable has 4 sqmm CPC touch voltage on fault becomes 164V
- 16 sqmm cable has 6 sqmm CPC touch voltage on fault becomes 167V
AJJewsbury:
230V supply.
- 1.5 sqmm cable has 1.0 sqmm CPC touch voltage on fault becomes 138
- 2.5 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 144V
- 4 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 167V
- 6 sqmm cable has 2.5 sqmm CPC touch voltage on fault becomes 162V
- 10 sqmm cable has 4 sqmm CPC touch voltage on fault becomes 164V
- 16 sqmm cable has 6 sqmm CPC touch voltage on fault becomes 167V
But that only holds entirely true if the entire earth fault loop consists of that type of cable - which typically it isn't. For a PME system for example you'd have a full sized PEN making up the 'Ze' part of the circuit - so diluting the increased voltage somewhat. Then you'd likely have main bonding at the intake which should in theory (and to some extent in practice) remove the p.d. along the supply PEN from what someone in the installation is exposed to. Actual numbers will vary considerably from each installation and fault to the next - but the general assumption seems to be that the mitigating factors like these usually balance out the increased voltage differences from the reduced c.p.c.s and so the 0.4s for 120-ish volts is still 'reasonable'.
- Andy.
gkenyon:Within what we used to call an equipotential zone, TT performs much better, and touch voltage is very small. Outside of that artificial construct, the touch voltage in a fault in TT systems approaches U0
I wasn't aware that it is no longer called the equipotential zone. The fact that you used the expression "what we used to call" indicates that there is no description for it but it must still exist.
I wasn't aware that it is no longer called the equipotential zone. The fact that you used the expression "what we used to call" indicates that there is no description for it but it must still exist.
I think it's just an admission that bonding doesn't create equipotentiallity - the laws of physics get in the way as bonding conductors don't have negligible impedance and the voltage difference along a c.p.c. during an earth fault (giving the potential difference between an exposed-conductive-part and extraneous-conductive-parts can be very significant.
- Andy.