V fault = Vsupply *(Rlive /(Rcpc +Rlive))
230V supply.
- 1.5 sqmm cable has 1.0 sqmm CPC touch voltage on fault becomes 138
- 2.5 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 144V
- 4 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 167V
- 6 sqmm cable has 2.5 sqmm CPC touch voltage on fault becomes 162V
- 10 sqmm cable has 4 sqmm CPC touch voltage on fault becomes 164V
- 16 sqmm cable has 6 sqmm CPC touch voltage on fault becomes 167V
All more than 120V...
More likely around this:
V fault = Vsupply *(Rlive /(Rcpc +Rlive))
230V supply.
ProMbrooke:More likely around this:
V fault = Vsupply *(Rlive /(Rcpc +Rlive))
230V supply.
- 1.5 sqmm cable has 1.0 sqmm CPC touch voltage on fault becomes 110V
- 2.5 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 95V
- 4 sqmm cable has 1.5 sqmm CPC touch voltage on fault becomes 88V
- 6 sqmm cable has 2.5 sqmm CPC touch voltage on fault becomes 70V
- 10 sqmm cable has 4 sqmm CPC touch voltage on fault becomes 64V
- 16 sqmm cable has 6 sqmm CPC touch voltage on fault becomes 50V
Yes but ... that only works indoors. And even there, slightly over 70 V is too much for 5 s ... perhaps even 1 s.
What about when you supply equipment outdoors, and have no control over the voltage at a person's feet as you might have within a building (what we used to term "equipotential zone")?
The worst case is a TT system, because the full U0 is available outdoors, and 1 s is way too long.
Next up comes a TN-S system where the installation is some distance from the transformer supplying it.
The actual answer, as Mike alluded to, is that it's an engineering compromise between what's practicable, and the likely risk of shock in a fault condition (larger conductors perhaps less likely to break, often in more robust wiring systems etc.).
kenyonYes but ... that only works indoors. And even there, slightly over 70 V is too much for 5 s ... perhaps even 1 s.
What about when you supply equipment outdoors, and have no control over the voltage at a person's feet as you might have within a building (what we used to term "equipotential zone")?
The worst case is a TT system, because the full U0 is available outdoors, and 1 s is way too long.
Next up comes a TN-S system where the installation is some distance from the transformer supplying it.
The actual answer, as Mike alluded to, is that it's an engineering compromise between what's practicable, and the likely risk of shock in a fault condition (larger conductors perhaps less likely to break, often in more robust wiring systems etc.).
In all of this I am assuming remote earth and a minimum body impedance of 1000 ohms. Zero bonding or equal potential taken into account.
I'm well aware the IEC used to allow (and still does to a degree) equal potential bonding as a means to manage greater disconnection time however this is not what I have in mind.
In a TN system voltage from the fault point to remote earth is far lower than is being assumed here. The transformer is far from an infinite source, it is rather weak.
It has nothing to do with compromise, rather the IEC knows voltage and body resistance will typically never reach values that will violate the IEC's body graph.
I'm going to go out and say that with circuits protected over 200-400 amps could easily get away with a 10 second disconnection time and this should be researched/considered further.
davezawadi (David Stone):ProMbrooke
Your equation and results do not make sense, perhaps you would like to correct the error in your potential divider equation, obvious because increasing the conductor size from 2.5 to 4.0 mm LOWERS the touch voltage. I will leave the correction to the student.
This is key:
Notice the assumption of C=0.8, meaning that on circuits 32 amps and under it is assumed the voltage at the source could dip to 184 volts or 80% of nominal, or at least 90% of nominal if part of C comes from being inside a structure with metal enforcments connected to the MET.
mapj1:
But that factor of 2 in the denominator of your equation 8 should be more like 1.5 in the case of twin and earth. Experience in the rest of Euroland is not so relevant here - in the UK our final circuits do not have full sized CPCs, (nor do quite a few in-building sub-mains either) and in built up areas we may have larger lower impedance transformers, indeed in parts of London 1MVA transformers are meshed and the LV network in the streets is not even fused (AKA "the solid system"). Then there are a great many tower blocks with a megawatt transformer in the basement, and then bigger office and mixed use buildings with HV going up to a transformer on every 5th floor or so (look at Canary Wharf for an example of that if you like)
In such cases your assumption that the supply droop has a dominant effect is not appropriate - it is mostly in the cables.
Note that just because something is written by a committee does not make it infallible - look at the number of times the regs get updated for proof of that. ( I've sat on telecoms standards meetings, I know how it works, and it has perhaps made me slightly cynical. )
I agree the incoming voltage will droop very significantly during fault for those rural sites fed by smaller (100kVA and down) pole-pig transformers, but they are more commonly earthed as TT anyway.
I'm not sure we should underestimate the touch voltages to city dwellers by assuming that all installations are like that.
There is an additional complication in a PME system, as the live voltage goes down the neutral comes up to meet it, so you have to be clear if you mean touch voltag relative to the CPC of the system, or to terra-firma earth voltage either at ground level as on incoming telephone cables etc.
M.
I agree, but remember, with MCBs you'll be hitting the instantaneous function even on your maximum permitted Zs. Only larger circuits (over 125 amps) will take time clearing, and those will cause at least some dip even on 1 MVA units. As such I still maintain the the source has a moderate to major effect on touch voltage.
London like France, New York, Chicago ect are exceptions though. These networks, in particular Con Edison's networks, can be regarded as being almost truly infinite. Evidenced by 500MCM (253mm2) cables burning clear in manholes with only mild, local dimming of lights. At the same time remote earth becomes far more scarce- sidewalks, poor conductive floors, bonded pipes and building steal all work to reduce touch voltage. The scenario of being outside on damp ground while holding a metal tool or electric grill in the back yard like out in the country become very slim.
I will agree with you that technical committees get it wrong or in the case of today influenced by the manufacturers, however I still hold the belief that 5 seconds is unlikely to present a danger in most cases.