Case 2. C.P.C. corrosion in T&E cable.

Today I stripped some 2.5mm2 T&E cables that run in 25mm black plastic conduit outside. The cable was continuous with no joints in the conduit boxes. The plastic conduit showed signs of being overheated in the sun at some period through the day. I had to cut the cable to make a joint, and I found that the C.P.C. showed signs of corrosion, just starting to show, nothing serious but enough to cause concern. I repeat, the cable had not been jointed when I found it and was continuous with the outer sheath intact throughout.


I can only conclude that the cables's outer sheath has let in moisture, even though the cables run in plastic conduit.


Is this why the Regs. do not advise running P.V.C. cables submerged in water? P.V.C. is not totally waterproof. 522.3.

https://www.belden.com/blog/broadcast/waterblocking


Z.

Parents
  • NYY cable looks tough for outdoor use. I would not bury it though as it has no earthed armouring. Normally P.V.C./P.V.C. cables seem to be o.k. run on brickwork if they have a chance to dry out after rain. I imagine that the cables in the plastic conduit that I discovered were subjected to a hot humid environment on occasions like in a sauna, which may have caused moisture ingress into the cable. The conduit had no drain holes at the lowest points.


    Z.
Reply
  • NYY cable looks tough for outdoor use. I would not bury it though as it has no earthed armouring. Normally P.V.C./P.V.C. cables seem to be o.k. run on brickwork if they have a chance to dry out after rain. I imagine that the cables in the plastic conduit that I discovered were subjected to a hot humid environment on occasions like in a sauna, which may have caused moisture ingress into the cable. The conduit had no drain holes at the lowest points.


    Z.